[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
NFPA 70E Training outcomes (Ref: Safety Training...)
Original poster: Sparktron01-at-comcast-dot-net
List
I attended this training several weeks ago (2 days). There were many
videos of severe injuries and fatalities arising from "Arc Flash/
Electrical Explosions", and several videos of staged electrical explosions
(up to 15kV -at- 5kA) that were frightening to say the least (see Bert
Hickman's video of the substation catastrophic KABOOM to have a similar
reality check). The interesting take homes and statistics from this
training are:
1. 80% of nationwide electrical fatalities involved qualified electrical
personnel (i.e. they had multiple years experience in electrical trade).
2. Many fatalities involved "gettting comfortable" in your job, and
eventually leads to shortcuts being taken (complacency). On HV gear this
is an invitation for disaster.
3. HV and high power LV equipment can have equipment failure, and if you
are near it when it lets go, all bets are off unless you have PPE
on. Water expands from liquid to vapor 1700 times it's liquid
volume. Copper vapor / plasma expands 64,000 times (!!!!!) its original
solid volume. Under a high energy fault condition, this will result in a
violent thermal explosion with molten debris, and electrical plasma being
ejected at high velocity, with a time duration of 0.5 sec or less. Impact
energies can be suffciently high to shear 3/8" steel bolts. Imagine
several thermite grenades and sticks of dynamite going off in confined
quarters simultaneously...
4. Many folks have died by bad meters, meter leads, or making an
ASSumption that the power was turned off and no back feed path existed. If
a DVM is not rated for class III (CB panelboard) service, and a high energy
HV transient causes an arc over internal to meter; can result in a meter
explosion. The moral of the story is DO NOT risk your life using a $3.00
Harbor Freight (or similar) DVM's, use an industrially rated meter if
working on high power/energy circuits that may be live. Also if you have
to replace the meter fuse, replace it with the EXACT replacement, they are
usually designed with higher then normal interrupting and voltage clearing
rating (AFAIK Fluke uses 17kA / 1kV ceramic cartridge fuse in ammeter
circuit as an example).
5. Circuit breakers should be mechanically exercised ONCE A YEAR. This
was a revelation to me, but with our TC's of various flavors pounding our
house panels, please take heed. The CB mechanism can be uncalibrated by
extended time running at 90-95% of breaker ampacity by internal
heating. This may preclude the breaker from operating at all. If you
operate the breaker and it does not "feel" right, or sounds "mushy" when
the contacts open and close; REPLACE THE CB. It is cheaper then replacing
your house!
6. Fuses are a much more reliable high energy interrupting means then
CB's. They are commercially available with interrupting ratings to 300kA,
and low-peak fuses will clear a high energy fault in less then 1/4 cycle
60Hz (4 millisecs). Low peak fuses also dramatically limit arc/flash exposure.
7. Use GFI's, they are lifesavers.
8. Wear cotton clothing rather then synthetics when working around HV or
high energy circuits, the synthetics when exposed to arc/flash can melt
into the skin and cause severe 2nd and 3rd degree burns.
9. Avoid working on HV circuits alone, use the "buddy" system.
Be safe out there...
Regards
Dave Sharpe TCBOR/HEAS, Chesterfield, VA. USA