[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
3 phase transformer on 1 phase
Original poster: "J. B. Weazle McCreath by way of Terry Fritz <twftesla-at-qwest-dot-net>" <weazle-at-hurontel.on.ca>
Hello Greg and coilers,
Here's the scoop on how to wire up a 3 phase transformer to
work on single phase power as promised. This method was
shown to me by an electrical engineer friend and I have
personally made use of it successfully.
73, Weazle
USING A THREE PHASE TRANSFORMER ON SINGLE PHASE
===============================================
I = Iron core of transformer
W = Windings on each leg of core (numbered)
S = Start terminal of windings
F = Finish terminal of windings
IIIIIIIIIIIIIIIIIIIIIIIIIIIII
IIIIIIIIIIIIIIIIIIIIIIIIIIIII
SWWWWWWW SWWWWWWW SWWWWWWW
WWWWWWW WWWWWWW WWWWWWW
WW 1 WW WW 2 WW WW 3 WW
WWWWWWW WWWWWWW WWWWWWW
WWWWWWWF WWWWWWWF WWWWWWWF
IIIIIIIIIIIIIIIIIIIIIIIIIIIII
IIIIIIIIIIIIIIIIIIIIIIIIIIIII
Only the windings on the outer legs are used, the windings
on the middle leg (No. 2) are not used. The principle of
the hookup is that you want the phasing of the outer legs
to be such that at a given moment the magnetic flux will
be north at the top of the left hand windings while it is
south at the top of the right hand windings. You'll see
that the two fluxes created by the outer leg windings add
together in the outside legs and horizontal parts of the
core, but they cancel each other out on the middle leg.
I'm assuming that the transformer has high voltage windings
in the 10,000 to 15,000 volt range and low voltage windings
of 240 volt or 120/208 volt. The connections are as below:
1) Locate and identify the start and finish of each winding.
There will be a primary and a secondary winding on each
of the three legs of the core. Determine which terminals
are the primary connections and which terminals are the
secondary connections. The high voltage terminals are
usually labeled H1, H2, and H3, while those of the low
voltage are labeled X1, X2, and X3. Also, the low voltage
terminals will have much heavier gauge wire coming from
the windings than the high voltage terminals.
You will likely find that the finish terminals of all of
the primary windings are connected together. You'll also
likely find that the finish terminals of the secondary
windings are connected together. If this is the case, it
indicates a Wye connection configuration and it can be
left that way. If not, proceed with the next steps.
2) Connect together the finish terminals of the low voltage
windings 1 and 3. If the finish terminal of low voltage
winding 2 is also connected, you can leave it that way,
or you can disconnect it. Connect together the finish
terminals of high voltage windings 1 and 3. If you find
that the finish terminals of high voltage winding 2 is
also connected, remove that connection.
3) Apply 120 volts AC by connecting one lead to the start
terminal of high voltage winding 1 and the other lead
to the start terminal of high voltage winding 3.
4) Measure the voltage between the start terminal of low
voltage winding 1 and the start terminal of low voltage
winding 3. You'll measure a low voltage, with it being
in respect to the transformer ratio. For instance, if
the primary is 12,000 volt and the secondary is 240 volt,
the ratio is 50:1 so you should measure about 2.4 volts.
5) A final test is to measure for voltage at the terminals
of windings 2, which should be very low or nil if things
are connected properly.
6) Once the tests are completed successfully, it can then
be connected into the circuit the right way around.