[This, while not directly Tesla Coil, may be of interest.
It fell of a professional lightning list.
best
dwp]
======================================================================
-------- Original Message --------
Subject: [LightningProtection] Got Ground?
Date: Mon, 05 Nov 2001 18:54:43 -0000
From: "R.T. Hasbrouck"
[Lightning safety discussions almost always include some reference to
grounding. Yet, many of the comments and/or questions I see indicate
to me that the concept of ground is often poorly understood. The
attached document provides an introductory overview of several types
of grounds, including lightning safety.
Rick O'Keefe has informed me that several experts reviewed and made
no further suggestions to the write up, so I am confident it won't
convey erroneous information.]
GROUNDING, AN OVERVIEW
R.T. Hasbrouck, EE, PE (Control Systems)
Core-group member
Although the term ground is repeatedly used, and misused, when
discussing lightning, I suspect some don't realize that not all
grounds are the same. The following is not a rigorous engineering
dissertation, but an attempt to highlight the different types of
grounds.
A true ground is an equipotential plane, which may be the Earth
itself (actually located somewhere beneath Earth's surface—the
British use the term "earthed" rather than "grounded") or a large
metallic surface. Ideally, the potential difference between a
grounding point and true ground will be zero volts, and all points
that are grounded will have zero potential difference between them.
Since current will flow through grounding paths and through ground
itself, the only way for potential differences to be zero is for the
impedance of the path to be zero. In the real world, the best that
can be hoped for will be low values of impedance.
Grounding for electrical power systems is quite different from a
radio-frequency ground, an electrostatic ground, or a lightning
ground. For electrical power systems, which operate at frequencies
close to dc, a metallic rod (having a low value of dc resistance)
driven into the earth works fine (refer to the National Electrical
Code for details). This ground is often referred to as a safety
ground. If an internal failure (fault) causes the "hot" power lead to
come into contact with the metal housing of an appliance, tool, or
piece of equipment, a person touching that housing will receive an
electrical shock. The severity of the shock will depend upon the
amount of insulation between the victim and ground. The "ground" with
which the victim is in contact might be a wet concrete floor,
metallic plumbing, or other grounded electrical equipment. To protect
against such shocks, electrically powered appliances, tools, and
equipment having metallic housings must be connected to the safety
ground. When so connected, fault current will flow via the safety
wire to ground, causing the metal case to be close to zero volts,
rather than at the full line voltage (assuming the safety ground
circuit resistance is sufficiently low). Safety ground conductors
need to be capable of carrying the full load current of the
associated circuit. Note that if the fault causes full load current
to flow, a fuse or circuit breaker should trip; if the circuit has a
ground fault interrupter (GFI), a small amount of current will trip
the GFI.
For equipment operating at radio frequencies, it is not always
necessary to have a direct connection to an equipotential surface—
capacitive coupling is often used to provide a low-impedance path to
ground for RF current.
Lightning, which is a current pulse, contains a broad spectrum of
frequencies—the center of the power spectrum is about 4.5 kHz, with
the upper limit reaching into the MHz range. Its peak return-stroke
current is extremely large (10s of thousands of amperes), typically
lasting for a hundred microseconds, or so. As the return-stroke
current pulse flows through the resistance of the earth it produces a
very large transient potential gradient across the ground. This
potentially lethal gradient—nominally 1,000 volts per meter—is known
as step voltage. However, even when the current is flowing in a
substantial metallic conductor (i.e., one having a very low value of
dc resistance) very large transient voltages are developed along the
conductor. Although resistance may be very low, e.g., less than 10
ohms, the inductance (L) of the conductor (nominally 1.5 microhenrys
per meter of conductor length) times the very high rate of change
(di/dt) of the current pulse produces transient voltages reaching
100s of thousands volts, or higher (V == I*R + L* di/dt). So, despite
the big emphasis on achieving a very low resistance ground, the
inductive effect predominates, resulting in transient voltages
significantly higher than those attributed to dc resistance of the
grounding system. A lightning grounding system must be capable of
accommodating extremely high peak currents, and present low values of
resistance and inductance. When grounding system resistance is
tested, the equipment operates at a very low frequency. The result,
which may look quite low, will actually be just the dc resistance
component. Huge (i.e., deadly and damaging) transient voltages will
be developed across the conductor while return-stroke current is
flowing. Finally, consider a ten-meter section of heavy copper
conductor connected to an earth ground. For lightning protection, two
systems are bonded to it, one at each end of the section. The dc
resistance between the two points is measured to be ten milliohms;
the inductance is 15 microhenrys. A 50th percentile lightning return
stroke of 24-25 kA, with a current rate-of rise of 40 kA/microsecond,
flows through the conductor. Peak current times dc resistance
produces approximately a paltry 240 V peak between the two "grounded"
points. However, the peak transient voltage resulting from the
conductor's inductance is 600,000 volts! The two supposedly grounded
systems are 600 kV apart, albeit only for a brief interval of time.
Equipment damage and serious injury or death are definite
possibilities, hence the reason for using single-point grounding.
Finally, consider the bonding of a fueling vehicle to a recipient
tank. The purpose for bonding is to ensure an equipotential
environment so that no electrostatic discharge can take place between
the tanker and the tank. Just the process of transferring fuel can
generate enough electrostatic potential difference to produce an
ignition-producing spark. In another situation, workers handling
sensitive explosives or sensitive solid state devices must not be
allowed to develop electrostatic charges on their bodies. Static
charge can reach multi-kilovolt-level voltages. However, unlike
utilities and lightning, the associated currents are very small—
nominally 100s of microamperes. Consequently, the resistance of the
discharge path can have a high value. People who work with
electrostatically sensitive components or explosives wear metal
watchbands bonded to the facility grounding system. To ensure that
workers so grounded won't be electrocuted if they accidentally come
in contact with utility power, a high-value, current-limiting
resistor (typically 1 megohm) is placed in series with the bonding
strap.
In conclusion, when discussing "grounding" it is very important to
know what type of ground is being considered, and to recognize that
ground is not always ground.