[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: Explain 3 Phase
Original poster: "by way of Terry Fritz <twftesla-at-uswest-dot-net>" <A123X-at-aol-dot-com>
So does that mean that between the hot holes in each set of two outlets there
is a 240v difference?or is that not the way it works?
In a message dated 4/27/01 5:18:08 PM Eastern Daylight Time, tesla-at-pupman-dot-com
writes:
One more time..... The electrical service supplied to 99.9% of American
>
> homes is single phase, 120/240 volt, 3 wire service. Single phase means ONE
> phase...period....not 2 phases 180 degrees apart. The service enters the
> house via a cable comprising two insulated (hot or line) conductors wrapped
> around an uninsulated, grounded, neutral conductor. The neutral conductor
> is connected to the midpoint of the secondary winding on the distribution
> transformer on the pole or the pad and connected solidly to ground. The
> voltage between the two line conductors is 240 and between either line and
> neutral is 120. The function of the neutral conductor is to carry the
> unbalanced portion of the load. If you had only identical 100 watt, 120
> volt light bulbs as the only loads in your house, and they were evenly
> distributed so the same number of bulbs ran on each line conductor, the
> neutral conductor would carry no current. The two line conductors are of
> opposite POLARITY compared to the neutral conductors. The same situation
> exists on a Y connected 3-phase bank. The neutral is grounded for safety
> reasons. One of which is that the maximum voltage from line to ground in
> your home is 120 volts. So, even if you stuck your finger in a 240 volt
> dryer outlet, you would feel a 120 volt shock, provided you had good contact
> with the ground. To experience 240 volts you have to stick both fingers in
> the outlet. DON'T TRY THIS! Hope this helps. Coil safe!