You wrote:
>
>>From SROYS-at-radiology.ab.umd.edu Mon Oct 16 08:44 MDT 1995
>>Received: from comm1.ab.umd.edu (comm1.ab.umd.edu [134.192.1.5]) by
uucp-1.csn-dot-net (8.6.12/8.6.12) with SMTP id IAA26459 for
<tesla-at-grendel.objinc-dot-com>; Mon, 16 Oct 1995 08:04:24 -0600
>To: tesla-at-grendel.objinc-dot-com
>From: "SROYS" <SROYS-at-radiology.ab.umd.edu>
>Date: Mon, 16 Oct 1995 10:01:33 EDT
>Subject: Contactor questions
>
>I just bought a couple of 3-phase, 3-pole, open-type AC reversing
motor
>contactors at a hamfest yesterday and I have some questions. The box
>says that the contactor is rated for 27A continuous use. Since each
>contactor has two relays and each relay has three contacts, does this
>mean that I could wire everything up in parallel and be good to go for
>up to 3 * 2 * 27A, or is the 27A rating for each relay rather than
each
>contact?
Yes.
>
>Also, the connection diagram is a little confusing and I haven't had
time
>to play with it yet, but I'm assuming that I CAN wire it so both
relays can
>be energized simultaneously and give me simultaneous parallel switch
>closures? How should I wire things up for 120V or 240V operation?
>Since 120V only has one hot line, can I run the one hot wire through
the
>relay (which would give me 6 parallel relay contacts to use), or
should I
>run both the hot and neutral line through (esentially one relay per
line)?
> Presumably with 240V, I should also run both hot wires through the
>relays?
>
If you can guarantee which is neutral and hot in your 120V wiring,
parallel all the contacts on the hot. Of course, use separate contacts
for 220V connection.