[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
Re: [TCML] X-ray cable best practices for feeder cable
Resonance can be quite wonderful, or, as Phil explains in his examples, very
destructive.
Resonance in your HV feeder cable is not something you want, so I avoid
using any feeder cable that is coaxial in nature, ie, has a ground
shield around it. X-ray cables were designed strictly for DC power
transmission and not for transferring AC power.
Been there, done that ----- and it cost me a pole xmfr!
Dr. Resonance
On Mon, Jan 5, 2009 at 9:25 PM, <FIFTYGUY@xxxxxxx> wrote:
>
>
> In a message dated 1/5/09 10:37:26 P.M. Eastern Standard Time,
> sparktron01@xxxxxxxxxxx writes:
>
> >I am now in the world of "Power Engineering", and I absolutely
> >concur with DC; I've seen evidence of it in Medium Voltage
> >(>600V, <15kV) systems.
>
>
>
> Dave, how about repeating your story of the direct current power cable
> with
> a pinhole burned through the insulation every foot? :)
>
> >One of our companies clients had a bad substation ground at
> >2.4kV L-L to a 1000 HP motor. Interesting to see a 45 deg
> >"crucifix" burned around a bonding bushing on a 600A
> >feeder conduit entering the MV MCC. MCC/Motor Ground
> >missing to substation ground, EXCEPT for MV cable shields
> >(not there from original installation, not our companies
> >installation); length of "burn/arc" flashing at least 3" long.
> >So this situation is EXACTLY like using a shielded X-Ray
> >cable in Tesla service.
>
>
>
> Switching (and other transients) can excite resonances in shielded cables
> and other stray capacitances which of course can cause the damage you
> describe.
> Worse is the problem of these resonances being excited by harmonics from
> non-linear loads.
>
> >On a delta system (no ground) with a "capacitive" single phase
> >arcing fault to ground, transient over voltages can exceed
> >8X V applied. If you doubt, check the IEEE "Buff" Technical
> >reference for details. I trust we all understand the implications
>
>
>
>
> >of applying ~1kVAC to a 120VAC branch circuit....
>
>
> That's why you stick arrestors and transient devices all over the place
> BTW, Dave, do you still have all those MOV's?
>
> >Proper grounding is important in house wiring, but MUST
> >be installed correctly at MV; a fire, catastrophic equipment
> >damage (even collateral to unrelated systems), or electrocution
> >will result if improperly installed.
> >
> >Imagine what would happen if a plant technician
> >had his bare hand on 1000HP motor while running, and a single
> >phase (or capacitive gradient) current occurred. At a minimum
> >a severe shock, or more likely death would have occurred.
> >I have made it a personal rule to never touch high horsepower
> >medium voltage motors while running for this reason...
>
>
>
> The root cause is the bad grounding. A 1/20 horsepower motor at 60V, or
> even
> less, can kill you just as dead.
> The worrisome part is the high-resistance grounding utilized in many
> medium voltage systems, or the intentional lack of grounding in many
> systems
> where downtime is more costly than safety. Then monitoring devices are
> supposed
> to prevent disasters. But I wonder if facilities with ungrounded systems
> change their procedures when they know they have a ground fault ("Don't
> touch
> anything until we can shut down next Saturday!"). Bad Things have happened
> when
> one ground fault a while later precipitates a second fault, and then a
> line-line fault occurs...
> Or in an electrolytic cell room, where grounding is also intentionally
> avoided to prevent accidents. Now *there's* a low-impedance source for
> you!
>
> -Phil LaBudde
>
> Center for the Advanced Study of Ballistic Improbabilities
> **************New year...new news. Be the first to know what is making
> headlines. (http://www.aol.com/?ncid=emlcntaolcom00000026)
> _______________________________________________
> Tesla mailing list
> Tesla@xxxxxxxxxxxxxx
> http://www.pupman.com/mailman/listinfo/tesla
>
_______________________________________________
Tesla mailing list
Tesla@xxxxxxxxxxxxxx
http://www.pupman.com/mailman/listinfo/tesla