Jim,
This is a very common arrangement actually. Most modern services that I
have worked with are a Wye, and most isolation transformers are
delta/Wye.
Ground the X0 of your Wye from the generator, and connect the three
phases to your delta primary. Then ground the X0 from your Wye secondary
also. They used to forbid this in the electrical code, (at least the
Canadian one anyway), but it is now the rule. You don't need to ground
your HV primary neutral, but it won't hurt either.
Leigh