Hi Phil,
Tesla list wrote:
Original poster: FIFTYGUY@xxxxxxx
In a message dated 5/1/06 12:37:55 PM Eastern Daylight Time,
tesla@xxxxxxxxxx writes:
>Yes, but there is no assumption. D.C. said "as the interior side of
>primary is at X1 (grounded) potential". That indicates, connecting X1
>to ground. That is clear.
Sorry, I'm a little slow, but that still doesn't clarify it to
me. If anything, this raises the additional issue of which end of
the *primary* winding is adjacent to the core or secondary winding.
Again, unless I'm missing some conventional labelling of pole pigs,
the worst case could end up:
One end of primary (LV winding), the end furthest from core, at
ground potential
Other end of primary (LV winding), the end closest to core or to the
secondary's (HV winding) HV end, at 240V
Neither end of the LV windings are at ground. They are floating. 240
Vac would be typical in the US connecting the LV across X1 and X3. X2
is left unconnected.
I see we got our X's and H's mixed up. Thanks for being persistent.
One end of secondary (HV winding), the end furthest from core, at
ground potential
Other end of secondary (HV winding), the end closest to the core or
to the primary's (LV winding) 240V end, at 15kV
Ideally, the core side should be at RF ground as this is the least
stressful situation. I connect H2 on my pig to RF ground..
Obviously this is the highest-stress situation, and best-case is the
complete opposite. My concern is calling the "H1" or "X1" labelled
ends of the windings the ones closest to the core or other winding.
Is there some convention that pig manufactures must follow when
labelling, or should a pig owner open and verify the connections?
Not a bad idea. Popping the lid and taking a look doesn't hurt. But
there is a standard for all distribution transformers. Looking at the
transformer so that the LV bushings are facing you, the HV bushing H1
is on the left and H2 is on the right. The LV bushing X1 is on the
right. X2 (neutral) is in the center and X3 is on the left. That is
the standard for a single phase distribution transformers.
The transformer core is connected to the case. I have left the core
as built and tie RF ground to the transformer case. Mains ground
stops at the control panel. In other words, I make sure RF ground and
mains ground are not connected (otherwise, you're going to get little
shocks here and there at the control cabinet).
You're concern is certainly valid because we got our X's and H's
mixed up. H2 should be at RF ground. This is the HV side closest to
the core and when looking at the LV bushings, H2 is the HV bushing on
the right.
On an (9, 12, or 15kV) NST, the interior ends of both HV
windings are both grounded to the core. Grounding one "bushing end"
puts 4.5, 6, or 7.5kV stress at the center of the HV windings to
core, where there was zero stress before. If the depotted NST HV
winding fails, and the core isn't still grounded, that puts the
core floating at 4.5 - 7.5kV where it normally would be at ground.
And thus it would put an abnormal stress to the primary winding
adjacent to the core. So in that respect I don't think that
connection scheme minimizes primary to secondary stress.
Yes, the center of the HV side is at the core. I'm talking about "if"
the NST is unpotted, that situation could be removed. Then it could
be setup just like a distribution transformer. But I don't unpot
NST's (too messy). Just a possibility if someone wanted to go that
route. The case of the NST would also be tied to RF ground. I set my
NST under the coil and tie RF ground to the case. Mains ground is
nowhere near and only back at the control.
Hope that helps clarify.
Take care,
Bart
-Phil LaBudde
-Phil LaBudde