[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re:re: Contactor question



Original poster: "David Rieben" <drieben@xxxxxxxxxxxxxxx>

Bart, all,

Thank you Bart and all others that quickly repsonded to
my question regarding contactors. The general consen-
sus seems to be just what I was thinking - no multi-pole
contactor's poles are perfectly synchronized and therefore
one set of the contact points may consistantly take the
brunt of the breaking of the inductive load. I started out
simply paralleling 2 of the 4 poles since I have a 60 amp
main breaker for my control panel cabinet. I noticed that
one set of the contact "poles" sparked a whole lot wores than
the other though and that's what got me to thinking that
they were indeed NOT synchronized. I ended up using all
4 poles in a series-parallel configuration thinking that this
may further distribute the inductive spark energy and it did
seem to help a little bit. I think that I would still prefer to just get
a contactor whose each individual contacts are at least
rated at the 60 amps though. And I mean 60 amps FLA
(full load amps, I assume) not 60 amps resitive load. The
30 FLA (40 amp resistive) contactor that I am currently using
was just given to me anyway so there'll be no big loss by up-
grading, only the cost of the bigger contactor itself.

David Rieben



----- Original Message ----- From: "Tesla list" <tesla@xxxxxxxxxx>
To: <tesla@xxxxxxxxxx>
Sent: Monday, August 15, 2005 12:41 AM
Subject: Re: Contactor question


Original poster: "Barton B. Anderson" <bartb@xxxxxxxxxxxxxxxx>

Hi David,

Yes, I know well what your are thinking here. But, the contactors do not all make or break at the same time. Thus, the last in line to open will see the "full" load for that brief moment. (Inductive loads are nasty on contacts of any size). Likely, this particular contact will always be the "slow one" and it will eventually weld closed if opened and closed during a load, which is the key to it's use.

I use a 50A contactor. It is controlled by the PLC and will open if the VFD has an error or for a few other reasons (dead man switch open, key off, PLC glitch, etc.). This is "error" mode and is the only time the contactor would actually open during a load. During normal operation, I always have the contactor on before putting V and I into the tranny. The contactor I use has had no problems so far. IMO, 30A is a bit small for these swinging pig loads. Even 50A ratings I would consider risky.

Take care,
Bart

Tesla list wrote:

Original poster: "David Rieben" <drieben@xxxxxxxxxxxxxxx>

Hi all,

Just a quick question about relay contactors. Let's say that I have
a 4-pole, 30 FLA inductive per pole rated contactor. Does this mean
that I will have up 120 amp inductive rating of the contact points if I
use all 4 of the poles in a parallel or series parallel fashion in a single
circuit to switch my pole pig transformer under a load?

Thanks,