[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
RE: Rewinding BIG transformer
Original poster: "Duke, Ronn (CCI-San Diego CCC) by way of Terry Fritz <twftesla-at-uswest-dot-net>" <Ron.Duke-at-cox-dot-com>
Jason,
With the formulas I have, assuming your 25 sq. in. core area, I came up with
60 turns on the primary and 7900 turns on the secondary with 240v in.
N = (k x E)/ A, where k=6.256 when f=60 Hz., or, k=7.507 if f=50 Hz
(6.256 x 240v) / 25 sq. in = 60.06 Primary turns
Turns per Volt = N/E
60.06 / 240v = .25 Turns per Volt
N=Number of primary turns
E=Primary Voltage
f=line-frequency
A=core cross-section Area
B=max.flux, in lines, Assuming 60,000 lines of flux
Secondary turns are determined with this formula:
ST = SV x 1.05 x TV
30,000v out x 1.05(losses) x .25 (turns/volt) = 7875 Secondary turns
ST= secondary Turns
SV= Secondary Voltage
TV= Turns per Volt on the primary
This is assuming an average of 5% core and wire losses.
I'm probably going to get hammered on this but I've consulted several
different sources, and they're all pretty close. Hope this helps.
Sparky
-----Original Message-----
From: Tesla list [SMTP:tesla-at-pupman-dot-com]
Sent: Sunday, March 25, 2001 10:22 AM
To: tesla-at-pupman-dot-com
Subject: Rewinding BIG transformer
Original poster: "Jason Johnson by way of Terry Fritz
<twftesla-at-uswest-dot-net>" <hvjjohnson13-at-hotmail-dot-com>
Hello,
Yesterday I got back from a state surplus auction that had equipment
from
around lower Michigan. I managed to score a huge transformer for
cheap (50
bucks!) there too. The transformer as it sits is good for stepping
2400 delta
down to 480 delta at 112.5 KVA (no thats not a typo). This thing is
huge! It
weighs in at 950 lbs (we had fun getting it off the truck, my back
is still
sore!) and is the size of a small refrigerator! It has a core area
of about 25
inches^2 and is the standard EI core type, only the core is about 2
feet long
and 2 feet tall.
What I was wondering was if I could rewind this beast for about 30kv
at 24 KVA.
The only thing is I want to do this as cheaply as possible (read: as
few turns
as possible). Solving the equation:
A=74*PV/(f*PT)
where:
A= cross sectional area of the core in square inches
74= guesstimated permeability of the core material (has worked well
for all the
transformers I have)
PV= Primary voltage
f= frequency
PT= Primary turns
for PT:
PT=74*PV/(A*f)
And putting 240 in for PV, 25 for A, and 60 in for f; I get 11.84
for PT.
Is this right? Only 12 turns for 24KVA? Are my calculations screwed
up? By this
same number I would only need 1500 turns for the secondary! I like
these
numbers, but I'm afraid that they're not right!
Comments?
Jason Johnson