[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

IDEC Smart Relay Update, National Electric Code



Original poster: "David Sharpe by way of Terry Fritz <twftesla-at-uswest-dot-net>" <sccr4us-at-erols-dot-com>

I have taken possession of 5 of these relays (FL1A-H12RCE).  Briefly recaping
they are a new micro-PLC with 8 digital inputs, and 4 hard relay (isolated NO)
outputs.  Inputs I5 and I6 are rated at 1kHz count capablility, and I7 and I8
are
0-10V analog input.  I built a VTTC controller with filament heating and real
time
grid and plate current monitoring.  The control ate only 50% of total relays
resources  :^).  The entire development kit including relay, software and
download
cable is ~$300.  I built a development station and tried on the real
article and
it
worked like a champ!  Even has five alphanumeric operator prompts (E.Stop,
Guards, Fils Heating, and Grid/Plate Over current Trip.  The amount of time
saved by reduced wiring and more flexible control is amazing.

I forwarded info from a National Electric Code refresher class to Jim Lux
(Hi!).

The object was to determine the pieces of the code that have legal "teeth" and
direct impact to TC building and construction in general.  The following
are the

definitions and code sections that impact our work.  This information is
provided
as is, and is truly not meant to belittle anyone's work.  The major abstract
points
of below post are:
1.  A disconnection means and overcurrent protection must be provided for
branch

    circuit loads (read Tesla Coil).   Feeders and protective equipment in new
    installations should not be loaded above 80% of capacity.
2.  Neon sign transformer "Farms" are explicitly disallowed in the code
     ("...transformer secondaries shall not be connected in series or
parallel..."
3.  From neon sign section of code, requires 1.5" to ground at 7.5kV.  This
    suggests that 3" separation is needed at 15kV.  I know there are many
    confounding variables (BIL of equipment, lightning exposure, power
capacity,etc)
    but this is first time reasonable distances in protected environments for
current limited
   HV equipment is mentioned.
4.  From induction and dielectric heating section, any capacitor larger then
0.1uF
     at a voltage of 250VDC or greater must be provided with suitable bleeder
    resistors.  This equates to any stored energies greater then 0.003 J.
5. If you want to check my comments, be sure to use the 1999 Code.  There has
been a
    massive revision between the 1996 (and earlier) and 1999 Code, to the point
that
   a cross reference table in the 1999 code had to be provided to find
applicable
   sections in earlier code(s).
6.  Again, not trying to start a flame war, and comments are welcome.  Each of
   the articles in the National Electric Code are included usually because of a
   casualty event (i.e. death, injury, or  property damage).

Regards

Dave Sharpe, TCBOR
Chesterfield, VA. USA
----------------------------------------------------------------------------
------------

National Electric Code and Relevance to Tesla Coil construction

WARNINGS:
1. The National Electric Code is NOT intended as a design manual
     for untrained persons.
2. “Good Engineering Practice” will often require more conservative
     design then the NEC states.  The NEC is a MINIMUM standard.
3. “Compliance with the NEC will result in an essentially hazard free
     installation, but not necessary efficient, convenient or adequate for
     good service or future expansion.”
4.  This information is provided “AS IS” with no warranty expressed
     or implied.  User assumes all liability with use.

Article 100 Definitions
Disconnecting Means
Overcurrent Protective Device (OPD)
Fitting
Equipment
Clearance
Utilization voltage
Qualified Person(s)
Overload
Overcurrent
Short Circuit
Ground Fault
Interrupting Rating
Ground
Grounded
Grounded conductor
Equipment grounding conductor
Grounding electrode conductor

Articles 110,200,400
1. Examination, installation, and use of electrical equipment
2. Identification of disconnection means
3. Working clearance (around enclosures)
4. Branch, service, and feeder circuits
5. Use and identification of grounded (neutral) and grounding  conductors
6. Ground Fault Protection
Working clearances Table 110-26a
Dedicated space (Article 110-26f)
 No storage of materials
 No piping, ducts, or foreign equipment allowed
Ingress, egress and panelboard clearances
Door Access; allow 90deg opening of doors (Article 110-26(a)(2), page 70-79
Illumination of work areas (Articles 110-26d & 410-4,5)

Protection from Live Parts (Articles 110-27a) “shall be protected by the
use of:
“
         Total enclosed enclosure
         Room (implied locked and access allowed to “QUALIFIED
         PERSONNEL ONLY”  )
`       Vault
         Physical Elevation
             600V or less  8 ft
             0.6 - 7.5kV  8 ft ­ 6 in
             7.5kV ­ 35kV  9 ft
             OVER 35kV  9 ft + 0.37 in / kV above 35kV

Over 600V utilization equipment will be posted by “DANGER-HIGH VOLTAGE”
      Placards
Grounded (neutral) conductors Articles 200-6(a)(b) identification
     Branch Circuits
     Conductor Identification Article 210-5
     Grounded (neutral) conductor ­ Article 200-6 -  colored with white or gray
overcoating
     Grounding (ground) conductor ­ Article 250-119 - colored with green or
green/yellow
         IEC/CE coloring
     Overcurrent protection ­ continuous and non-continuous loads (Art.
210-20(a) )
Continuous Load ­ Load is expected to continue for 3 hours or more.

 Rate overcurrent protection at 125% of continuous load + 100% of
non-continuous
load.
 Size overcurrent protective device at value or next larger standard trade
size.

Disconnecting Means
Article 225-31… Means shall be provided for disconnection of all conductors
that

      supply or pass through the building or structure.
Article 225-32… Means shall be readily accessible at point of entrance of
      conductors .
Articles 230-71,72… Services to a building shall consist of not more then 6
     switches or circuit breakers. ( 6 arm movements or less to isolate all
power
     to a building or system)

Articles 240, 310-Overcurrent Protection
1. Proper Sizing
2. Circuit breakers versus fuses application
3. Matching wire size
4. Preventing electrical explosions
5. Interrupting Fault Current
Overcurrent Protection ­ Article 240
     Tap Rules (Article 240-21 and exceptions), 10 feet, 25 feet, over 25 but
less
     then 100 feet, over 100 feet
Location of OCD -- Article 240-24
      OCD’s not located where exposed to physical damage
      OCD’s not located in vicinity of easily ignitable material
Article 240-83
      Every circuit breaker having an interrupting rating other then 5kA shall
be so
      marked with rating.

Grounding ­ Articles 250
1. Grounding overview
2. Understanding grounding language
3. Grounding electrode conductor
4. Grounded conductor
5. System grounding
6. Enclosure grounding
7. Grounding connections
8. Different type grounds (analog, digital, power)
9. Portable equipment
10. Sizing of ground conductors
11. Sizing of bonding conductors

Article 250-2
Circuits and systems grounded to limit:
     Voltages due to lightning, EMI/RFI
      Line surges
      Unintentional contact with higher voltage lines
      Stabilize circuit voltages during normal operation
All conductive materials bonded together to prevent local differences of
   potential  (all metal cases on a system as an example)
Facilitate OCD operation with a ground fault

Article 250-6
  Grounding system shall be installed in a manner to prevent the flow of
  objectionable currents.  Alterations to stop currents:
       Discontinue one or more grounding connections
      Change locations of grounding connections
       Interrupt continuity of conductive path interconnecting the grounding
         connections
       Other actions satisfactory to authority having jurisdiction (inspector)
             Comment:  Changing grounds from a daisy chain (“looped”) to
                              a common point star grounding methodology
used for

                              analog, signal, digital and power grounds is an
example
                              of the above.

Article 250-20 systems required to be grounded
      Where system is separately derived
      Transformer is not grounded
      Supplied by overhead conductors outside of a building
      Maximum voltage to ground on ungrounded (power) conductors is 150
       volts or less

Article 250-24
       Location of grounding connection between grounded (neutral) conductor
      and the grounding (ground) electrode shall be made at the service
equipment
      (Neutrals and grounds MUST be isolated in control panels and utilization
      equipment, UNLESS a new source is being derived.)

Article 250-24
      Grounded conductor shall be bonded to case of all service disconnection
means.
      (All equipment in a Tesla system with a metal case MUST be grounded to
       service equipment ground; and ISOLATED from RF ground)

Article 250-24 (Table 250-66)
     Grounding conductor not smaller then the electrode conductor size in
     Table 250-66.  Equipment grounding conductor size is listed in
      Table 250-122

Article 250-50
      Grounding Electrode System shall be made up of
      Metal water pipe
      Metal Frame of building
      Concrete encased electrode
      Ground ring
      Driven ground rods

Article 250-56
    Ground rod resistance shall be 25 ohms or less.  Additional ground rods
   separated by at least 6 feet can be used to augment (reduce) grounding
   resistance)

Article 450 ­ Transformers
   General rule is transformers should have overcurrent protection at 250%
   of full load transformer rating, if no secondary overcurrent protection is
   used.  Under certain conditions and exceptions (authorized personnel
   only, restricted space, etc. ) up to 600% full load overcurrent settings are
   permissible.  Transformer saturation effects are nearly always seen at load
   levels of 250-300%, so 250% is a good working figure with NEC support.

Article 490 ­ Equipment over 600V Nominal
  Entire article applies, particularly to high power pole pig or PT powered
systems,
  clearances, interlocks engineering controls, isolation and enclosure
requirements
  should be carefully studied.
       Comment:  The “excessively” large clearances are necessary to guarantee
                         adequate BIL rating of air insulated equipment in
indoor/outdoor
                         environments.  If switching or lightning
transients are
not a design
                         issue, and equipment will be housed in an indoor dry
environment;
                        spacing may be significantly reduced (see Electric Sign
Spacing,
                        article 600-32 below for less than 15kV wiring).

Chapter 6, Special Equipment
Article 600 ­ Electric Signs and Outline Lighting

600-5b -- Branch circuits shall not exceed 20A, and will be dedicated to
lighting
     load.  Computed load per branch circuit will be a minimum of 1200VA

600-6a ­ Sign will have dedicated disconnect, can be located within or outside
     of line of sight, should be lockable in all cases

600-7 ­ Signs will be grounded.  Listed metal flexible conduits, or metal
liquid

   tight conduits shall be used as a grounding means as long as conduit
   lengths do not exceed 100 feet.

600-23 ­ Transformers and Electronic Power Supplies;
      All will have GFI with following exceptions
      - Transformers with isolated secondaries shall have maximum open
        circuit voltage of 7500V or less
     - Transformers with integral porcelain or glass secondary housing
        for tubing requiring no field wiring of secondary circuit.

     Voltage will not exceed 15kV nominal under any load condition, voltage
    to ground will not exceed 7.5kV under any condition from any output
    terminal.

    Transformers or electronic power supplies will have a secondary
    circuit current rating of not more than 300 mA.

     Secondary connections will not be connected in series or parallel
 << NO NST “farms” ALLOWED >>

     Transformer or power supply must be marked to indicate that it has
     secondary fault protection.

600-32 ­ Neon secondary conductors over 1000V nominal.

 Wiring methods ­ wiring to be run in approved raceway or on insulators

 Conductors will be rated for voltage, not smaller then #18 AWG, and have
minimum temp rating of 105 deg C

 No sharp conductor bends allowed (corona, dielectric loss)

 Conductors to be spaced 1-1/2” MINIMUM from each other and all other
 objects other then insulators or neon tubing.
 Comment:  This may be a good working rule for TC equipment that
          HV conductors will be no less then 1-1/2” between energized
          conductors and ground and 3” between energized conductors.
          This spacing is only valid for voltages up to 15kV between energized
          conductors and 7.5kV energized conductor and ground.

 Insulators and bushings shall be rated for purpose

 Dwelling occupancies ­ Equipment exceeding 1kV shall not be installed
in or on dwelling occupancies. <<NOTE>>

Cable length shall not exceed 20 feet in metallic conduit or tubing and
50 feet in non-metallic conduit or tubing.

Article 660 X- Ray Equipment

 Guarding, enclosures, conductors, interlocks and controls all applicable
due to similarity of hazardous voltages and conditions

Article 665 Inductive / Dielectric Heating  -- (Vacuum Tube/Solid State Tesla
Coils
   Defacto Rules)

 Enclosures ­ Completely enclosed, non combustible and deadfront
controls construction.

Doors or detachable panels shall be used for access.  Where doors access
compartments with greater then 500-1000VAC/DC, locking means or interlocks
will be provided, above 1kV AC/DC mechanical interlocks or locking means
and electrical interlocks will be provided.  Detachable panels not normally
used

for access will be fastened in a manner to make them inconvenient to remove.

DANGER ­ HIGH VOLTAGE ­ KEEP OUT shall be posted on all
compartments with voltages greater then 250VAC/DC, and where unauthorized
personnel may contact energized parts

Bleeder resistors shall be used on all capacitors exceeding 0.1uF having
voltages greater then 240V to ground. This includes auxiliary supplies for bias
voltages, tube keying etc.  Interlocked access doors will be used on coils
(work

coils/induction heating) with voltages above 150VAC, or at any DC potential
above ground
         Comment:  0.1uF -at- 250VDC = 0.003J (3mJ)  This hazard level is
                          probably chosen due to startle involuntary reaction
conditions
                          which could cause secondary injuries (lacerations or
cuts), or
                          throw body/limb onto high(er) power conductor(s),
possibly
                          resulting in additional severe/lethal injuries.

Grounded and bonding per Article 250 will be used.  Wire sizes will be #18 or
larger.  High voltage terminals will be guarded to prevent accidental contact.
Step
down transformers for controls or auxiliary (filament) circuits will have
primary
overcurrent protection, sized per Article 450.

Additional General Rules (wiring/workmanship):
1.  Wires in a raceway are required to have insulation class of highest present
     voltage in raceway.  This is generally why separate conduits are run for
power,
     control, and signal conductors.

2.   Most installations are now installed with THHN and this class
insulation is

      rapidly becoming a national standard, due to size reduction, higher
temperature
      class.  #18 of smaller AWG is generally 1kV class insulation, #16AWG or
      larger is 600V class insulation.

3. Overloading of conductors in certain conditions is allowable by code
provided

    that inverse timing is allowed to limit thermal rise on conductors.
Electrical
    installations are normally for continuous operation (greater then 3 hours),
while
    Tesla Coils even under most aggressive use are intermittent operation.  So
power
    conductors sized to code requirements in intermittent duty (100% ampacity)
    should provide adequate  safety factors under most use conditions.

NOTE:  This list is a first blush attempt to link legal requirements of
National
Electric
Code to Tesla Coil construction practices.  Many of these rules make good
common

and engineering sense.  Again, realize that these rules are ENFORCEABLE under
the
United States Uniform Building (BOCA) Codes, and generally a dwelling can
not be

occupied until electrical inspection confirms these “terms and conditions”
(i.e.
the
electrical installation) have been met.  Also again be aware the NEC is a
minimum
standard, building to a higher standard usually involves more cost and is
generally
avoided by contractors, unless the end owner is willing to deal with the cost
adders.
Also, the requirements of the Occupational Safety and Health Administration
(OSHA),
particularly in regards to Personal Protective Equipment (PPE), Labeling, and
Training
are significantly more stringent then requirements in NEC.

 This information is provided “AS IS” with no warranty expressed or implied.
User(s)
assume all liability with use.

D. E. Sharpe
3/8/2001, Rev. 01-- 3/16/01